Hello,
Can two VFD 4160V cable assemblies (overall OD of one cable assembly is 2.33-inch) be pulled into concrete duct bank with 6-inch schedule 40 PVC (6.065-inch ID) 400-feet between manholes with no bends? Per NEC 2008 Chapter 9 Table I, two conductors can be pulled in provided they do not exceed 31% for all conductor types. Performing quick percent conduit fill calculation using these dimensions I calculate a conduit fill of 29.5%. Therefore, I believe I should be able to make this pull but not sure. Can anybody share some insights on this?
Can two VFD 4160V cable assemblies (overall OD of one cable assembly is 2.33-inch) be pulled into concrete duct bank with 6-inch schedule 40 PVC (6.065-inch ID) 400-feet between manholes with no bends? Per NEC 2008 Chapter 9 Table I, two conductors can be pulled in provided they do not exceed 31% for all conductor types. Performing quick percent conduit fill calculation using these dimensions I calculate a conduit fill of 29.5%. Therefore, I believe I should be able to make this pull but not sure. Can anybody share some insights on this?