Hello,
Can two VFD 4160V cable assemblies (overall OD of one cable assembly is 2.33-inch) be pulled into concrete duct bank with 6-inch schedule 40 PVC (6.065-inch ID) 400-feet between manholes with no bends? Per NEC 2008 Chapter 9 Table I, two conductors can be pulled in provided they do not exceed 31% for all conductor types. Performing quick percent conduit fill calculation using these dimensions I calculate a conduit fill of 29.5%. Therefore, I believe I should be able to make this pull but not sure. Can anybody share some insights on this? :)
 

Besoeker

Senior Member
Location
UK
Hello,
Can two VFD 4160V cable assemblies (overall OD of one cable assembly is 2.33-inch) be pulled into concrete duct bank with 6-inch schedule 40 PVC (6.065-inch ID) 400-feet between manholes with no bends? Per NEC 2008 Chapter 9 Table I, two conductors can be pulled in provided they do not exceed 31% for all conductor types. Performing quick percent conduit fill calculation using these dimensions I calculate a conduit fill of 29.5%. Therefore, I believe I should be able to make this pull but not sure. Can anybody share some insights on this? :)
Not sure what you mean by cable assemblies.
Could you describe what is meant by cable assembly please?
 