MWBC arc fault breaker

Status
Not open for further replies.
is it a 2 pole breaker or can I use 2 single pole breakers with a handle tie?

I am not sure, but I don't think 2 single pole breakers will work. Well, mechanically they will work but electrically I don't think so.
 
Actually each breaker must have a neutral pigtail connection for power, but may not need to actually supply/sink the circuit neutral current.
If the AFCI includes a GF detector, you are forced to use a double pole breaker with a common neutral connection. (That does work for an MWBC).
 