MWBC on Delta Service

Status
Not open for further replies.

LRB

Member
Location
Interior Alaska
I am installing several MWBC on a Delta Hi Leg service. Hi leg is B phase and all circuits are between A and C phases. Will my neutral be counted as a CCC? On a 208 Y service I believe it would be due to the 120 degree phase angle.
 
My answer is that the neutral is not a CCC. The A-N and B-N will be 180 degrees out of phase with each other, and the neutral will only carry the unbalanced current between the A and the C.
 