romex jockey101
Member
i went into a panel that i was about to run a home run from after looking through the panel i noticed a nuetral wire was burned arouned the insulation very badly. it was a mwbc terminated in a tandem breaker.the circuit was 15 amps and was feeding 2 general lighting circuits in a garage and office.. when i went into the office i noticed a 120 plug heater witch they were using it draws about 12 amps...then i went into the garage and the home owner had a table saw pluged in draws about 13 amps ...bc the tandem breaker only sits on phase a it does not cancel out the unbalanced load and the 14 awg could not handle the load ..so i made shure that one leg was on phase a and and i put the other leg on phase b....this was very dangerous and could of started a fire...mwbc on tandems are very dangerous