For 1p-20a circuits and sharing neutrals 1" EMT Homerun pipe with #10's out of panel.
I CAN'T pull 12 circuits because that would be 9 hots, 4 neutrals(1 for every 3 circuits) and 1 ground. That would be 17 wire and I'd be over 40% fill
If I pull in 11 circuits that would be ok?
Make sense?
I CAN'T pull 12 circuits because that would be 9 hots, 4 neutrals(1 for every 3 circuits) and 1 ground. That would be 17 wire and I'd be over 40% fill
If I pull in 11 circuits that would be ok?
Make sense?