horsegoer said:
Okay if I have 120/208 lighting and I can share neutrals will a 12/3 MC w/ground handle 3 circuits?

No, you will need a 4 conductor w/g cable.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
horsegoer said:
Why is that?

Think about it, you would have to have A,B,C conductors, a neutral conductor, and an EGC.

Roger
 

jmsbrush

Senior Member
Location
Central Florida
horsegoer said:
Okay if I have 120/208 lighting and I can share neutrals will a 12/3 MC w/ground handle 3 circuits?
Horse how is it going in the estimating shop?
I remember when you first signed on here you said you have never been an estimator and you have no electrical experience at all?

I really just don't see how that works.
I mean no ill harm from my statements and I do wish you the best.
An estimator can make or break a company.
I think it would be good for you to work in the field for a couple of years ,if you physically can, to get some experience, It would be good for you're career.
 