petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- engineer
Take a look at this photo and tell me what you think the markings mean.
I read the 60A max CB as applying only to CSA group motor applications, while in NEC applications the max CB rating in a group motor application would be based on NEC requirements, which would appear to be based on 430.53. I am still mulling over what the max rating of a CB would be in a group installation.
As best I can tell, there is no requirement in the NEC to ever have a CB less than 15A on a motor, regardless of size, so what the heck does the 6A Fuse/CB thing mean? I can't even get a 6A CB in a MCCB so does that mean you can only use this MSP on fuses? Or that if you use it on a CB it can only be used in group motor installations?
Assuming that the "acc. NEC" means that whatever the heck is in the NEC is what governs the max. SCPD size, it appears that the appropriate NEC requirement would be 430.53 (C) which has 5 requirements that have to be met. It appears there is no easy way to get around the first two requirements unless there is an actual max. CB marking on the device. Since there isn't one, how in the heck can you even use these things in a group installation other than by using 430.53 (A) or (B) which are pretty restrictive. there just does not appear to be any obvious way to take advantage of 430.53(C) at all.
I read the 60A max CB as applying only to CSA group motor applications, while in NEC applications the max CB rating in a group motor application would be based on NEC requirements, which would appear to be based on 430.53. I am still mulling over what the max rating of a CB would be in a group installation.
As best I can tell, there is no requirement in the NEC to ever have a CB less than 15A on a motor, regardless of size, so what the heck does the 6A Fuse/CB thing mean? I can't even get a 6A CB in a MCCB so does that mean you can only use this MSP on fuses? Or that if you use it on a CB it can only be used in group motor installations?
Assuming that the "acc. NEC" means that whatever the heck is in the NEC is what governs the max. SCPD size, it appears that the appropriate NEC requirement would be 430.53 (C) which has 5 requirements that have to be met. It appears there is no easy way to get around the first two requirements unless there is an actual max. CB marking on the device. Since there isn't one, how in the heck can you even use these things in a group installation other than by using 430.53 (A) or (B) which are pretty restrictive. there just does not appear to be any obvious way to take advantage of 430.53(C) at all.