"My microwave keeps tripping the breaker!"

Status
Not open for further replies.

480sparky

Senior Member
Location
Iowegia
Hmmmmm, I wonder why..........



This morning's service call:

Loose%20PushMatic%20Connection.jpg
 
It's because they used pink instead of black? :p

Is that only 1 strand under the lug?
 
Maybe the fact that the circuit breaker buss lug is incandescent is causing a thermal trip?

Oh, well, everything eventually leaks, cracks, corrodes, loosens or seizes.
 
That's a pretty looking Pushmatic breaker. ...........

There was an inspection tag on the panel dated 2014. HO said it was for the kitchen remodel. My guess is it was a new breaker installed then.

I had the HO put a cup of water in the micro and turn it on.. Amp meter read 14.7-15.0 amps. That's when I noticed the glowing connection. I shut it off, removed it and inspected both the breaker and buss bar for heat damage (very minimal), and reinstalled it as the the glowing connection was caused be the original installer didn't seem to have even put a screwdriver to the buss screw. Tighten it down, and life is good.

I wish all service calls were this easy. Took more time to remove & reinstall the cover than to diagnose.
 
There was an inspection tag on the panel dated 2014. HO said it was for the kitchen remodel. My guess is it was a new breaker installed then.

I had the HO put a cup of water in the micro and turn it on.. Amp meter read 14.7-15.0 amps. That's when I noticed the glowing connection. I shut it off, removed it and inspected both the breaker and buss bar for heat damage (very minimal), and reinstalled it as the the glowing connection was caused be the original installer didn't seem to have even put a screwdriver to the buss screw. Tighten it down, and life is good.

I wish all service calls were this easy. Took more time to remove & reinstall the cover than to diagnose.
And with those big gloves, safety face shield, etc, etc it is cumbersome.
 
I don't have enough fingers and toes to count the number of times I've come across either loose or cross-threaded breaker to buss screws like that.
 
There was an inspection tag on the panel dated 2014. HO said it was for the kitchen remodel. My guess is it was a new breaker installed then.

I had the HO put a cup of water in the micro and turn it on.. Amp meter read 14.7-15.0 amps. That's when I noticed the glowing connection. I shut it off, removed it and inspected both the breaker and buss bar for heat damage (very minimal), and reinstalled it as the the glowing connection was caused be the original installer didn't seem to have even put a screwdriver to the buss screw. Tighten it down, and life is good.

I wish all service calls were this easy. Took more time to remove & reinstall the cover than to diagnose.
OK, at first I didn't see any problem, and was wondering what we were to be looking for it looked like maybe camera flash reflection on that area.

Infrared image would have been obvious though:)
 