NEC requires that you meet the environmental demands.
Nema-3R tests use a simulated wind-blown rain. Nema-4 use a hose from all angles. Ordinard "compression" type connectors do nothing to seal the interface between the fitting and the enclosure.
For ordinary outdoor locations, this is only a problem on the tops of enclosures; in other orientations, the unsealed area will tend to shed rain of its' own accord.
Where water may come from other directions -say, during a washdown- a Myers' hub ought to be used all around the enclosure.
I consider a Myers' hub to provide adequate bonding. The o-ring is only on one face; the other is serrated. Only in an explosion-proof installation, or when using fiberglass enclosures, do I see a need for bonding jumpers.