FionaZuppa
- AZ
- Part Time Electrician (semi retired, old) - EE retired.
I ran into a odd issue at my own place.
One ckt (1pole gfi-ocpd 20A) was working fine for past 2+yrs until recently. The ocpd trips every other day for no good reason that I can tell.
The ckt runs outside underground all PVC, about 100ft of 12ga. At the end is a outdoor fridge rated 2A that cycles on/off 24x7. Four ceiling fans each rated 0.8A (but stay off, controlled by bluetooth canopy controllers).
I have local discos (switches) to the fridge and fans. Leave the switches on, goto reset ocpd, and the ocpd will either quickly trip, OR, it stays on for 3-4sec then trips. Here's the very odd part, reset ocpd and immediately try the manual Test button, and get nothing, then eventually ocpd trips off in the 3-4sec range.
I then turn off the discos, come back to ocpd and reset it, it sticks on ok, and the Test button works ok for 10 consecutive tests.
I then go turn on the discos, fridge starts to run, no ocpd trip.
Bad ocpd ??
Can you explain the odd no-trip when pressing the Test button?
Bad ocpd ??