busman
Senior Member
- Location
- Northern Virginia
- Occupation
- Master Electrician / Electrical Engineer
All,
If you remember my post about the church with the single phase service and the three phase gear. Photos below show what I had expected all along. Details in words:



It is pretty clear this used to be three phase service with CT. Is it possible the PoCo dropped the three phase for some reason? This church was probably a very low usage customer (only on Sundays). There is 3-phase along the road less than 80 yards away where this is fed from. I could try to get it back to 3-phase, but they may have appliances that won't like 208V (AC units).
My question is, if I remove the clearly illegal jumper between A and C phases and replace with a three opening Polaris tap, will there be any other violations?
Thanks,
Mark
Note: Somehow the last photo got flipped left for right. The feeders really enter from the left.
If you remember my post about the church with the single phase service and the three phase gear. Photos below show what I had expected all along. Details in words:
- No CT's in the CT cabinet
- 200A service conductors
- Illegal jumper in the MDP
- Didn't trace the red taps in the MDP mains



It is pretty clear this used to be three phase service with CT. Is it possible the PoCo dropped the three phase for some reason? This church was probably a very low usage customer (only on Sundays). There is 3-phase along the road less than 80 yards away where this is fed from. I could try to get it back to 3-phase, but they may have appliances that won't like 208V (AC units).
My question is, if I remove the clearly illegal jumper between A and C phases and replace with a three opening Polaris tap, will there be any other violations?
Thanks,
Mark
Note: Somehow the last photo got flipped left for right. The feeders really enter from the left.