Good evening everyone. I have a mystery. I have been in the electrical field in commercial and residential for 32 years and never seen this and cannot figure it out.
Installed a stand by generator for a customer in a remote location. About 1 hour from any sizable city. We started today off with running control wiring for AC load management. This required getting into the crawlspace. Eww.
While down there my helper came out and said he thought the gas line shocked him. Yeah right. It's Sat and your hung over. Get to work.
Later on while making the connection to the gas tank I felt a very mild tingle. I almost thought I was imagining it. After 32 years carple tunnel is taking its toll and I often get nerve jolts that feel like electrical shocks. Kept working amd didn't feel it again.
An hour or so later while tying the load management contactor in my helper again said he felt a tingle. So this time we started investing.
Found the 3/4" propane gas line that's buried about 12 feet from the home runs under directly into the crawl space. Outside when measuring from the pipe to the bond wire we ran from the service we get between 1.5 and 3.2 volts. It varied. Under the house about 0-10 feet in it gets up to 6 volts. As you continue back under the house it begins to drop and goes to the 2-4 volt range.
We went as far as pulling the meter and disconnecting the generator incase there was bleed over from the battery into the grounds. No matter what we still get that same voltage range on the pipe in the same places.
I thought maybe it was an electrified fence that's solar powered. Nope. Turned it off and still there.
To deepen the mystery. We ran 3/4" polyethylene from the tank to the generator. There is only metal contact at one point near the generator it's about 2" into the ground. I got the same voltage there. Once I tied the gas bond back in I did not again read voltage at the generator but still had it at the pipe under the house.
I thought maybe bad neutral causing imbalance or trying to use the bond system as a grounding point but the voltage line to line is 230 and each leg is 115.5-116 even.
IIs it possible there's some sort of reaction going on on the gas pipe in the ground causing voltage? I'm also thinking maybe it's something AC system related as the furnace is gas. Possibly bleed through from capacitor when the power was off and leaking into bond wire when power is on?
Were headed back Monday and are going to disconnect all gas lines from appliances and disconnect the gas where it enters the house to see if we can get it to go away. I'm probly going to try and run a new polyethylene run to where the galvanized leaves the ground and see if that clears it.
Any advice is appreciated. Thanks in advance.
Installed a stand by generator for a customer in a remote location. About 1 hour from any sizable city. We started today off with running control wiring for AC load management. This required getting into the crawlspace. Eww.
While down there my helper came out and said he thought the gas line shocked him. Yeah right. It's Sat and your hung over. Get to work.
Later on while making the connection to the gas tank I felt a very mild tingle. I almost thought I was imagining it. After 32 years carple tunnel is taking its toll and I often get nerve jolts that feel like electrical shocks. Kept working amd didn't feel it again.
An hour or so later while tying the load management contactor in my helper again said he felt a tingle. So this time we started investing.
Found the 3/4" propane gas line that's buried about 12 feet from the home runs under directly into the crawl space. Outside when measuring from the pipe to the bond wire we ran from the service we get between 1.5 and 3.2 volts. It varied. Under the house about 0-10 feet in it gets up to 6 volts. As you continue back under the house it begins to drop and goes to the 2-4 volt range.
We went as far as pulling the meter and disconnecting the generator incase there was bleed over from the battery into the grounds. No matter what we still get that same voltage range on the pipe in the same places.
I thought maybe it was an electrified fence that's solar powered. Nope. Turned it off and still there.
To deepen the mystery. We ran 3/4" polyethylene from the tank to the generator. There is only metal contact at one point near the generator it's about 2" into the ground. I got the same voltage there. Once I tied the gas bond back in I did not again read voltage at the generator but still had it at the pipe under the house.
I thought maybe bad neutral causing imbalance or trying to use the bond system as a grounding point but the voltage line to line is 230 and each leg is 115.5-116 even.
IIs it possible there's some sort of reaction going on on the gas pipe in the ground causing voltage? I'm also thinking maybe it's something AC system related as the furnace is gas. Possibly bleed through from capacitor when the power was off and leaking into bond wire when power is on?
Were headed back Monday and are going to disconnect all gas lines from appliances and disconnect the gas where it enters the house to see if we can get it to go away. I'm probly going to try and run a new polyethylene run to where the galvanized leaves the ground and see if that clears it.
Any advice is appreciated. Thanks in advance.