I am designing switchgear being used as a common output for paralleling (3) 1200KVA, 480V, 3-Phase, unity power factor UPSs. The configuration is for N+1 UPSs, so the downstream load is only anticipated to be max 2400kW; thus, 3000A bussing meets the max intended load. UPS output breakers in this switchgear are sized for the individual UPSs.
Even though downstream load isn't anticipated to grow and there is not enough mechanical cooling to support load growth either, I cannot say for sure what the future might hold. With the (3) UPS output breakers, it could be that the load increases and the parallel UPSs provide beyond the 3000A rated bus. By this, I believe I have no choice and have to rate the switchgear bus for 5000A.
This is similar to switchgear being used for paralleling multiple generators - the bus needs to account for maximum power available. I have heard others argue the UPSs and generator controllers may be programmed to avoid going over maximum design load, but I don't believe the code or UL would find these to be acceptable means of protection. I find this condition similar to gear containing main breakers with trip units - even though you can dial down the trip unit, the bus rating still needs to meet or exceed the frame rating of the main breaker.
My Question: There are instances in the code such as 220.60 for noncoincident loads. While I understand this reference is downstream of protection, I am wondering if anyone knows of similar code exceptions for my design condition.
Even though downstream load isn't anticipated to grow and there is not enough mechanical cooling to support load growth either, I cannot say for sure what the future might hold. With the (3) UPS output breakers, it could be that the load increases and the parallel UPSs provide beyond the 3000A rated bus. By this, I believe I have no choice and have to rate the switchgear bus for 5000A.
This is similar to switchgear being used for paralleling multiple generators - the bus needs to account for maximum power available. I have heard others argue the UPSs and generator controllers may be programmed to avoid going over maximum design load, but I don't believe the code or UL would find these to be acceptable means of protection. I find this condition similar to gear containing main breakers with trip units - even though you can dial down the trip unit, the bus rating still needs to meet or exceed the frame rating of the main breaker.
My Question: There are instances in the code such as 220.60 for noncoincident loads. While I understand this reference is downstream of protection, I am wondering if anyone knows of similar code exceptions for my design condition.