A UPS (singular) is always (at best!) N.
N+1 is usually used in relationship to modular UPS systems, or paralleled UPSs, where there is one more module or UPS than is required, and so if that fraction of the working system fails, you've still got the ability to supply full power. So for example, a 200KVA load may be serviced by three 100KVA paralleled UPSs, any two modules will do, one left over. If you had four 100KVA modules, you would have N+2, as any two could fail and you would still be OK. Note there is an assumption here that the UPS "system" can fail in parts whilst still operating as a whole. Sometimes this works, sometimes the whole thing dies. I generally don't like N+ systems as I've had to clean up after a couple of these things have failed. A failed N+ system is a dead system.
Better than N+1 modular or paralleled UPSs is 2N, where you have two separate UPSs feeding two separate distribution systems (note this requires each item of load equipment to be dual fed also), so the entire chain can fail, and the load is still supplied. For your hypothetical 200KVA load, you thus need a pair of 200KVA UPSs.
Note the difference in nomenclature between N+(some number) and (some number)N - they are very different beasts. You can do N+ for a Tier 3 facility, but to get Tier 4, you need the compartmentalization offered by the 2N approach. This may seem like a mountain and a molehill, but its a very big (and expensive) deal.