I am trying to figure out the best way to address this issue.
I have a small cabin completely wired with a 100 M/B loadcenter.
At this time there is no utility power available so the owner has installed a manual transfer switch and is feeding source #1 from a 30 amp/120v output on a portable generator. Source #2 is an 120v 20 amp GF receptacle on an inverter on a stand alone battery-solar system.
I have no intentional neutral-ground bond in the T/S or the loadcenter (there is continuity but the path is unknown at this time).
The GF receptacle on the solar output is not operating and there is no N-G bond on the generator 30 amp TL receptacle.
I need to establish a N-G bond to assure a ground fault return and my initial thoughts are that I need to have a N-G connection at the inveter and generator and switch the neutral through the T/S.
(A bond at the T/SD or panel will cause the solar 120v output GFCI to trip)
I have a small cabin completely wired with a 100 M/B loadcenter.
At this time there is no utility power available so the owner has installed a manual transfer switch and is feeding source #1 from a 30 amp/120v output on a portable generator. Source #2 is an 120v 20 amp GF receptacle on an inverter on a stand alone battery-solar system.
I have no intentional neutral-ground bond in the T/S or the loadcenter (there is continuity but the path is unknown at this time).
The GF receptacle on the solar output is not operating and there is no N-G bond on the generator 30 amp TL receptacle.
I need to establish a N-G bond to assure a ground fault return and my initial thoughts are that I need to have a N-G connection at the inveter and generator and switch the neutral through the T/S.
(A bond at the T/SD or panel will cause the solar 120v output GFCI to trip)