Typically, yes, it is permissible. The vast majority of notification appliances we install (that don't have a speaker component) are 2-wire devices. There are some 4-wire devices out there, but just don't pick those. We only install them as replacements for existing devices that have failed.I have a job where the larger rooms show combo horn/ strobes while the smaller rooms are strobe only. Is it permissible to run both off the same NAC circuit or should each be an individual circuit?
I’m wondering if there’s anything in the code against it more than anything?NAC circuits are typically limited by total current draw and voltage drop.
Are the strobes still synced this way?Typically, yes, it is permissible. The vast majority of notification appliances we install (that don't have a speaker component) are 2-wire devices. There are some 4-wire devices out there, but just don't pick those. We only install them as replacements for existing devices that have failed.
Strobe syncing is governed by the fire alarm control unit. Typically you can set a NAC via programming for sync or non-sync, and pick one of the more popular protocols while you're at it (Gentex, System Sensor, and Wheelock to name three). I will note that you can't mix appliance brands on a circuit, and usually, not on a panel.Are the strobes still synced this way?