I noticed the newer single gang 18.8 nail ons have quite large knock out I usually just put 1 #12 each knock out, is there any code you cant put two. But on the double gang with clamp I assume they intend for one cable each clamp.
jetlag
thanks tool
thanks tool
In the knock outs, you can put 2 cables in, if it has clamps, you can only put 1 cable per clamp.
~matt
Boy thats odd only 1 reply , I was getting worried people only put one in knock out so they didnt really know if could use 2 . I didnt want to have to pull some out. It just seemed to me be better to use 2 #12 than have the big gapping hole when 1 conductor is used in k o . The k o were not as big on the blue boxes , these are the black ones big blue is stocking now , you also get .8 more cu in over the blue 18 cu in.
Dennis Alwon
Chapel Hill, NC
Electrical Contractor
Generally I will use one cable per hole but I have used 2 cables per hole in a pinch. I believe some of them are rated for 2 cables just as some connectors will allow 2 cables.
jetlag
thanks dennis
thanks dennis
I prob should pull them out, it is just roughed right now, because I dont know where to check the box rating , its only a few boxes, anyway the wires are easier to strip if not on top of each other in same k o
jxofaltrds
Mike P. Columbus Ohio
ESI
How does .8 cu in help us?
Hendrix
New England
You don't strip the wire before you put it in the box?
jxofaltrds
ESI
This sounds like an electricity 101 quiz question
1 extra space beyond an allowed box fill makes a device easier to install
2 if a box only lacks .8 to install another cable, adding .8 to box allows it
3 the more box space the merry
ans : all of the above :)
How does #2 apply?
(3) 14-2 + device = 18.0 cu in
(2) 14-3 + device = 18.0 cu in
12-2 + 12-3 + device = 18.0 cu in
How does .8 cu in help?
jetlag
How does #2 apply?
On a 15 amp branch circuit a nail on box with a blank cover is used for a junction box and contains 3 # 14-2 nm cables and 1 #12-2 UF cable . To help prevent voltage drop the 12-2 uf was used to run to a remote storage building. Find the minimum cu in required for the nail on box.
(correct answer 18.75 cu in ) Darn I can use that 18.8 box for something :)
jxofaltrds
ESI
(3) 14-2 = 12
(1) 12-2 = 4.5
EGC = 2.25
And no device
Thank you for the math lesson.