An Industrial Control Panel wired as follows:
1. The load side of a 250Amp Circuit breaker is connected to the primary side of a Power Distribution Block (PDB) using 250MCM wire (rated at 255Amp).
2. From the Power Distribution Block there is a 12GA tap (rated at 25A) wired to to a 25Amp fuse.
All of these components are located inside the Industrial Control Panel. The 12GA tap conductor connected between the secondary of the PDB and the line side of the 25Amp fuse is less than 10FT.
A remote heater is connected to the 25Amp fuse. The conductor used to make the connection between the 25Amp fuse that is located inside the control panel and the remote heater ... is it considered a tap, a branch circuit conductor or a feeder?