MCA is minimum
MOCP is maximum
The specs for a glycol chiller indicate MCA 11 & MOCPD 18. Is it permissible to use the next standard size CB (20A)?
Who is the manufacturer? Sounds fishy to me as 18A is not a standard fuse or CB rating. If the minimum circuit ampacity is 11A, I'd most likely go with a 15A OCPD. However, try and get a cut sheet and do your own calculation to get the MCA and MOCP values.