I'm confused by the nameplate ratings on some busway tap boxes I'm seeing. They have 30A 80%-rated breakers but the nameplate says 30A - shouldn't it be 24A?
I also see dual-output units with two sets of 30A breakers with each drop cord sized for 30A, and they're still rated 30A - shouldn't they be rated 48A?
My understanding is that the nameplate should reflect the total allowable maximum current that the device can deliver, not the breaker rating.