Hi Folks,
Question here about service calculation when there's a device with specifications that include a LOWER minimum breaker size than the nameplate rating.
I'm looking at a Frigidaire induction stove that's going into an existing dwelling, so I'm using 220.83, but I'm interested in the question more generally, since this situation might arise with other devices.
In the manufacturer's specs they indicate:
Minimum circuit required: 40A @240, single phase
and yet, on the machine, the nameplate rating is clearly indicated:
15.5kW @240 ---> which is 65A!
For the service calculation, can I limit the machine's demand to 40A @240 = 9.6kW, or does the nameplate rating have to be used, in which case you're reserving space on the service that might only be used for a brief while until the breaker tripped?
Anecdotally, I've been doing a year-long load study that suggests these machines in practice don't draw more than around 32A.
Ricko
Question here about service calculation when there's a device with specifications that include a LOWER minimum breaker size than the nameplate rating.
I'm looking at a Frigidaire induction stove that's going into an existing dwelling, so I'm using 220.83, but I'm interested in the question more generally, since this situation might arise with other devices.
In the manufacturer's specs they indicate:
Minimum circuit required: 40A @240, single phase
and yet, on the machine, the nameplate rating is clearly indicated:
15.5kW @240 ---> which is 65A!
For the service calculation, can I limit the machine's demand to 40A @240 = 9.6kW, or does the nameplate rating have to be used, in which case you're reserving space on the service that might only be used for a brief while until the breaker tripped?
Anecdotally, I've been doing a year-long load study that suggests these machines in practice don't draw more than around 32A.
Ricko