Hey all, I'm a new member and this is my first post. I know this site is primarily for questions related to US installations and the NEC, but I was hoping I could appeal to some members that may have some insight into requirements in Canada. Even some rationale from the NEC may be helpful. So here's what I got.
I work for an OEM that makes power supplies. We recently shipped a system that utilizes a transformer with a 480 Delta primary. It's not a UL listed piece of equipment, so we enlisted a field evaluation service that approves equipment for general safety to SPE-1000 (a CSA safety code). He required us to change the nameplate input voltage from 480 to 480/277. My thought is that the nameplate should reflect the rating of the equipment, and the equipment requires 3 hots and a ground. His reasoning is that the equipment is approved for a Wye 4 wire system, but that doesn't mean a neutral is required to be run to the equipment. I can't wrap my head around his reasoning. To me it seems it may cause some confusion for an installer who may look at that nameplate and run a neutral when one isn't required.
So my question is, does his reasoning make sense to anyone here? Could you explain it to me?
Hopefully I've been clear enough, just let me know if I need to provide any more info.
I work for an OEM that makes power supplies. We recently shipped a system that utilizes a transformer with a 480 Delta primary. It's not a UL listed piece of equipment, so we enlisted a field evaluation service that approves equipment for general safety to SPE-1000 (a CSA safety code). He required us to change the nameplate input voltage from 480 to 480/277. My thought is that the nameplate should reflect the rating of the equipment, and the equipment requires 3 hots and a ground. His reasoning is that the equipment is approved for a Wye 4 wire system, but that doesn't mean a neutral is required to be run to the equipment. I can't wrap my head around his reasoning. To me it seems it may cause some confusion for an installer who may look at that nameplate and run a neutral when one isn't required.
So my question is, does his reasoning make sense to anyone here? Could you explain it to me?