mkenney
Member
- Location
- Syracuse, NY
- Occupation
- Solar Engineer
I'm trying to figure out how to determine the minimum AIC rating needed for a line side tap disconnect for a National Grid (NY) account. For all of our residential solar project that require a line side tap, we use a 2P, 60A, 240V, 22kAIC rated circuit breaker and have had no issues from inspectors on this. Recently, we had a NYSERDA inspection and they noticed that the main breaker of the homeowner's main panel was a 200A, 25kAIC rated breaker (Eaton BWH 200A, 25kAIC). Therefore they failed our inspection because our AC disconnect AIC rating didn't match that of the main panel's breaker. We are trying to contest this inspection but need to have something from National Grid stating what that AIC rating needs to be.
Does anyone know how to get this rating or calculation from National Grid? I have called several times, spoken with half a dozen different people, have emailed the distributed generation email, and left multiple questions and comments within the National Grid portal. I have either not gotten a response back or the person has never heard of an AIC rating.
Does anyone know how to get this rating or calculation from National Grid? I have called several times, spoken with half a dozen different people, have emailed the distributed generation email, and left multiple questions and comments within the National Grid portal. I have either not gotten a response back or the person has never heard of an AIC rating.