We are planning to install a 1300kW natural gas generator set at our facility. The utility put a metering station on our premises. The pipe coming out of the ground is run to a pressure regulator. This regulator has a 4" pipe outlet and is set to 5 psig. After the regulator is the metering components and then a flange. We are planning to run a 4" steel pipe from this flange point to another point near the generator. Near the generator the pipe will end at another flange. We will go from this flange to the generator with some flexible corrguated pipe with SS braid.
Question: Do the areas surrounding the flanges and meters need to be considered Class I Div II Group D? Is 5 psig on a 4" pipe enough to meet the requirements of NEC 500, that is - flammable gas in sufficient quantities to produce an explosive or ignitable mixture in the event of a leak from the flanges and/or meters? I think it is, but our safety department is pushing back on me.
Question: Do the areas surrounding the flanges and meters need to be considered Class I Div II Group D? Is 5 psig on a 4" pipe enough to meet the requirements of NEC 500, that is - flammable gas in sufficient quantities to produce an explosive or ignitable mixture in the event of a leak from the flanges and/or meters? I think it is, but our safety department is pushing back on me.