Does anybody have some order of magnitude cost numbers to make a case for using a 500 kWatt Diesel or natural gas generator vs the cost from the grid???
...
A 500kw generator is going to use ~35 gal/hr at full load. 35 x $2/gal = $70/hr
...
Probably ought to be conservative use the 1/4 load figure. Note that the consumption isn't linear, the generator is less efficient at partial load. Also $2per gallon is a great price for diesel these days.
Thus (using current average US price of diesel): 11gal/hr *$2.4/gal / 125kW = 21cents/kWh
That's higher than almost every figure in this chart, although certain tiers or time of use rates might be higher.
The answer to the question really depends on whether the capital costs for either the grid or the generator have already been paid for. As far as 'orders of magnitude' go, the costs are within one.
Yeah I was thinking of regular unleaded being about $1.90 a gallon here... diesel is closer to $2.50.
Even if the generator and associated equipment were free, the maintenance and fuel costs have to be higher than grid power. I'm sure some high paid engineering types for companies like ALCOA (that use an enormous amount of electricity) have already figured it out; afaik, they are tied to the grid, tho there may be POCO incentives and subsidies that skew the true price of power.
The page I linked assumed grid connection and sellback of unused electricity, and that the waste heat can be used elsewhere on site. For it to be competitive in price, the infrastructure for both has to be in place. and we know the generator and gear arent going to be free.
You have to watch using NG if you have large "step loads" (starting and stopping large motors would be one example)....NG does not handle those types of loads near as well as diesel does.Skip the diesel, use NG.
You have to watch using NG if you have large "step loads" (starting and stopping large motors would be one example)....NG does not handle those types of loads near as well as diesel does.
The last time I was looking at Cat generators, the supplier said that the fuel system for NG generators does not respond as well as diesel generators for a large increase in load...he was talking about 25% or more of total load. Not sure if the VFD would make much difference.That's interesting. What is it about the operation of NG-fueled generators that makes them problematic in that case? What percentage of generator capacity would be considered "large"? Wouldn't the use of VFD's reduce the issue?
Let's say a generator can last 20,000 hours. To put things into perspective, a car going 60 mph will travel 300,000 miles in 5000 hours.
20,000 hours is about 2 1/4 years, if the generator is always running. So, in addition to maint. costs, figure total replacement every 2 1/4 years.
Let's say a generator can last 20,000 hours. To put things into perspective, a car going 60 mph will travel 300,000 miles in 5000 hours.
20,000 hours is about 2 1/4 years, if the generator is always running. So, in addition to maint. costs, figure total replacement every 2 1/4 years.
with regular maintenance and rebuilding they can pretty much last indefinitely.
I seem to recall the first GE gas turbine unit lasted 30 some years before it was taken out of service. not because it failed but because it was just not efficient enough to be worth running compared to getting a new one.
IIRC, gensets intended to be in use 24/7 are very different quality from those intended to run for a couple days or even a couple weeks for backup purposes.
All the ones I have seen were turbines. I have never seen a continuous use or base line generator using a piston engine as a prime mover. If there is such a thing I would like to see a picture of it.