Hi, I have a quick question...
I am providing a 50kw generator for a school that will be used for egress lighting only. Since this falls under NEC Arcticle 700 as an Emergency System, I pretty much am limited to a diesel unit since I need 2 hours of on site fuel.
I remember reading something a while back that I couldn't use a natural gas gen with a utility hook up since that fuel source was considered interruptible.
Does this make sense?
Thanks...
Tom M.