Our Local AHJ had open meetings for contractors in respects to North Carolina and what to look out for with changes in 2008', and noting whats been put on hold. I beleive a few threads have already addressed State issues. Thanks Roger!

These are some of what our Local (Durham) Inspectors will be looking for, and anyone In NC can also use as a guide line. Others here can also gain some insights, thus this Thread/Post.

A friend got a copy of this letter and he knows I'm eat up with the forum.
This is a basic summary of what was covered in the Code over-view meetings of 2008 NEC-70 - North Carolina.

Mike Holt also listed thru a moderator these (key) changes in the FAQ area, of this forum and I beleive it can also be found in the left column of his home page.

110.16 Arc Flash labels for equipment

110.26 Panic Hardware for doors within 25? for equipment rated 1200 amp and larger

210.4(B) Multiwire branch circuits require simultaneous disconnecting means

210.4(D) Multiwire branch circuits require grouping of conductors in panel

210.8(A)(2) No GFCI exceptions for garage receptacles

210.8(B)(5) GFCI for receptacles within 6? of sinks

210.12(B) AFCI expansion Delayed until Jan 1st 2009

210.52(E) Balcony 20 sq. ft > require receptacle

250.32(B) 4 wire to second building

250.94 3 terminals for intersystem bonding at service equipment (includes second Building)

300.4(E) No under roof decking raceways within 1??

310.15(B)(2)(C ) Derate roof conductors

310.15(B)(6) Main power feeder

334.80 Derate cables through bored holes

338.10(B)(4)(A) SE cables 60 degree C ampacity

342.30(C) Support raceways over 18? long

406.8 Weather resistance receptacles delayed until Jan 1st 2009

406.11 Tamper resistant receptacles

408.36 Lighting & appliance panel boards deleted.

410.130(G) Fluorescent luminaries disconnecting means

422.52 water cooler GFCI receptacle

680.71 Hydro massage tub GFCI must be readily accessible

Enjoy
 
Thanks for taking the time to put that together.

110.26(C)(3) was in the 05 as 110.26(C)(2). Why will the NC inspectors be looking for panic hardware now???
 
You know , I don't know why!

You know , I don't know why!

Well I guess, it was a review of the subject matter (article) that they, the AHJ felt was important to review, and sudo turns into a hey pay attention/overview/refresher. :smile:
And your Welcome!
 
I didn't not Check every sub-paragraghs of each article that was listed, and thanks for noting any mistakes!

If I do this again, I will use all the resources to correctly present the exact information relating to articles as listed in the NEC-70 2008' verses just listing what was a copy of letter.
 
cadpoint said:
I didn't not Check every sub-paragraghs of each article that was listed, and thanks for noting any mistakes!

If I do this again, I will use all the resources to correctly present the exact information relating to articles as listed in the NEC-70 2008' verses just listing what was a copy of letter.

Not an issue, I was just wondering if it wasn't enforced before.
 