Near Miss Relating to Isolation

TVH

Senior Member


See link above.
Good example of the need to test circuits via voltmeter to verify zero energy state.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The very reason we added HOA switches for all controlled motors in one plant i worked at. That purpose being the verification of the lockout for non-electrical work. The hand position bypasses all interlocks other than the motor overload relay in the motor starter.
The procedure is try-lock-try. You go to the equipment and try to operate it there. Once you see the equipment operate, you lock out the equipment power source. Then you return to the HOA and put it in hand again, and if the equipment does not operate, you can do mechanical work on the locked out equipment.

Electrical work always requires verification of the de-energized state and cannot rely on not seeing the equipment operate with the HOA in hand.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
Watch out for hidden power sources too. I had a switchgear that the utility turned off the transformer, I verified the gear was dead, proceeded to connect an EPO switch, got a little jolt! Found a very small sticker on the switch that a capacitor was used in that circuit for backup power for the shunt trip. Must have been custom ordered, as I have never run across the same thing before, or since.
 