I'm hung up on properly sizing Type P cable (rated for 100C), and explosion proof motor, and a 75C terminal. Ampacity rating for the cable comes from IEEE 45-2002.
As you can see, the cable is way overkill for the actual current requirement, but is the smallest allowable size per NEC 430.22(G). Where I get hung up is the application of 110.14(C), which states that "the temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device." I exceed the terminal temp rating at 75C (20A), but will NEVER come close to this current during normal nor overload conditions.
Am I allowed to use this cable, but must consider circuit ampacity to be 20A? Section (C)(1)(a)(4) tells me I can use the cable, provided the ampacity of such conductors does not exceed 75C. This requirement seems to not apply since actual usage will never heat up the terminal.
| Motor FLC | = | 6.7 | A |
| x125 | % | ||
| Required Conductor Ampacity | = | 8.4 | A |
| 14 AWG @ 100°C Rating | = | 25 | A |
| Derating @ 55°C Ambient | x0.9 | ||
| Derated ConductorAmpacity | = | 22.5 | A |
As you can see, the cable is way overkill for the actual current requirement, but is the smallest allowable size per NEC 430.22(G). Where I get hung up is the application of 110.14(C), which states that "the temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device." I exceed the terminal temp rating at 75C (20A), but will NEVER come close to this current during normal nor overload conditions.
Am I allowed to use this cable, but must consider circuit ampacity to be 20A? Section (C)(1)(a)(4) tells me I can use the cable, provided the ampacity of such conductors does not exceed 75C. This requirement seems to not apply since actual usage will never heat up the terminal.