You might be correct, but how would you know for sure?
I would agree the equipment termination on the bus pads would need to be rated according to its ambient temperature that it is installed in.
Siemens has been asked about the limitations on
temperature for user?s cable connections to switchgear for
many years. ANSI/IEEE C37.20.2 (for metal-clad switchgear)
and ANSI/IEEE C37.20.3 (for metal-enclosed interrupter
switchgear) indicate that the temperature in the cable
termination compartment should not exceed 65 ?C when
the equipment is operating at its full continuous current
rating with the switchgear in a location with an ambient of
40 ?C. In ANSI/IEEE C37.20.2-1999, this temperature limit
inside the cable connection compartment is indicated in
clause 5.5.5, excerpted below:
5.5.5 Temperature limitations for air surrounding
insulated power cables
The temperature of the air surrounding insulated cables
within any compartment of an enclosed assembly shall
not exceed 65 ?C when the assembly is
a)
Eq
uipped with devices having maximum current rating
for which the assembly is designed.
b)
Car
rying rated continuous current at rated voltage and
rated power frequency.
c)
In an ambient air t
emperature of 40 ?C.
NOTE ? This temperature limitation is based on the use
of 90 ?C insulated power cables. Use of lower temperature
rated cables requires special consideration.
This has caused some users concern because this would
suggest that cable ampacity must be adjusted downward
due to excess temperature. We think this is not necessary in
most cases.