NEC 110.14 (C) Conductors with temperature ratings higher than specified for termination shall be permitted to be used for ampacity adjustment correction, or both.
Let say we have a conduit with 4 current carrying conductors. The correction factor is 80%. ( Table 310.15 (c) (1)
The current is 70 amps.
According to the code we shall use the 60 degrees but allowed to use a HIGHER rated wire ( THHN) to make the adjustment.
How would you determent what size THHN wire to use then ?