I will pose my question as an example.
A 225 kVA (480 VAC) transformer wil be installed in the state of AZ outdoors in a 50C ambient. I plan to run one large conduit from a 480 VAC panelboard to the transformer.
I prim = 225 / .48 / 1.73 = 271 amperes
125 % of I prim = 1.25 * 271 = 339 amperes
The minimum feeder size shall be (2) per phase 4/0 THWN-2 CU
310.16 - 90C column (4/0 AWG) = 260 ampere
Derate 50C = 82%
310.15(B)(2)(a) 80% (4-6 current carrying conductors)
Minimum Feeder Size = 2 * 260 * .82 * .8 = 341 amperes > 125% I prim, 339 (Code compliant)
Termination Verification
310.16 75C column (4/0) = 345 amperes
Derated 50C = 75%
Minimum Feeder Size = 2 * 230 * .75 = 341 amperes 1> 25% I prim, 339 (Code compliant)
Question
Do I need to derate by 75% for the termination verification part of this calculation to be code compliant?