NEC 2017 - 110.26 (5) Separation from High-Voltage Equipment.
Where switches, cutouts, or other equipment operating at 1000 volts,
nominal, or less are installed in a vault, room, or enclosure
where there are exposed live parts or exposed wiring operating
over 1000 volts, nominal, the high-voltage equipment shall be
effectively separated from the space occupied by the low
voltage equipment by a suitable partition, fence, or screen.
What is considered exposed live part for this new rule in NEC 2017? Can a substation (15kV primary, 480/277V secondary, 500kVA, 3PH xfmr)
be located in the same room with other low voltage panels (480V, 208V) as long as clearances are met? Or the substation needs to have its own room?
Thank you!