A anbm Senior Member Location TX Occupation Designer Mar 2, 2017 #1 Small electrical closet has a 208/120V electrical panel, located 2 feet across from room door, door to swing out when opens, will this comply with NEC 110.26(A)(1)? It is a wood door by the way.
Small electrical closet has a 208/120V electrical panel, located 2 feet across from room door, door to swing out when opens, will this comply with NEC 110.26(A)(1)? It is a wood door by the way.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Mar 2, 2017 #2 If the door is 30" wide and swings open so that the panel is in that 30" space, you should be fine.