Shujinko
Senior Member
I have proposed installation of 2 transformers with their respective disconnects in a mechanical room. There is a HVAC duct above the proposed location for the transformers that is 6'-1" above finished floor. In my eyes this is in violation of NEC 110.26(A)(3) which requires 6'-6" clear height from the floor for workspace. But a colleague brought up a good point to me. How do electricians/engineers get away with stacking transformers one above another. In some cases if the transformers are mounted on racks the transformers are one above another, and in some cases as close as 1' or 2' away from each other. Is my proposed installation of the 2 transformers (not stacked) under an HVAC duct that is 6'-1" above finished floor a violation of NEC 110.26(A)(3)? Is my colleague's point about stacked transformers a violation of NEC 110.26(A)(3)?