C clsarmiento Member Jun 18, 2013 #1 Is the 1200A equipment rating cumulative or any one piece of equipment?
jumper Senior Member Location 3 Hr 2 Min from Winged Horses Jun 18, 2013 #2 Not sure I understand the question correctly, is this a GFPE question? As far as additive for,in general, OCPDs-no.
Not sure I understand the question correctly, is this a GFPE question? As far as additive for,in general, OCPDs-no.
C clsarmiento Member Jun 18, 2013 #3 My question is: Does the 1200 amps rating applies to any one (or more) pieces of electrical equipment in the room, or the cumulative (total) of all equipment resulting in 1200 amps or more.
My question is: Does the 1200 amps rating applies to any one (or more) pieces of electrical equipment in the room, or the cumulative (total) of all equipment resulting in 1200 amps or more.
david luchini Moderator Staff member Location Connecticut Occupation Engineer Jun 18, 2013 #4 It means any one piece of equipment rated 1200A or more.