NEC 110 -

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Construction has installed two small dry type lighting transformers and Panelboards on a Unistrut rack directly below gas lines and air lines. There’s no liquid within these pipes - is this a violation of NEC 110?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The panel yes, the transformers no. The piping is in the dedicated equipment space unless it's greater than 6' above the panel.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The panel yes, the transformers no. The piping is in the dedicated equipment space unless it's greater than 6' above the panel.

Thanks infinity.
The 2 transformers are stacked directly above the two Panelboards. The pipe runs approximately 2 feet above the two XFMRs at roughly 14’ above finished slab. The top of Panelboards are at about 6 feet + below the pipe - should be good to go


Sent from my iPhone using Tapatalk
 