Experts,
I am little bit confuse on this and I hope you, the experts can enlighten me on this.
I have a 200A Main Service Panel by Murray/Siemens. The Bus Bar is 200A and has more than 20 breaker slots for breakers. The Main Breaker is a 4-pole 200A.
By 120% rule, if I have an AC feed by a solar system, I can only use a 40A backfeed breaker.
However, I read from somewhere, the author said the total amps of all the breakers can not exceed that 120% rule. I don't think that is correct. The fact is I have 16 branch circuit breakers, a 40A breaker for AC and 70A breaker to a sub panel in my garage that is already over 300A.
What I really think is, if my total usage at any time is more than 200A, the main breaker would simply trip, correct?
In my case, I am not using a lot of power at a time, I believe I can downsize my 200A Main Breaker to 150A, and that will enable me to use a 80A solar backfeed breaker to the Main Service Panel, correct?
Thanks
I am little bit confuse on this and I hope you, the experts can enlighten me on this.
I have a 200A Main Service Panel by Murray/Siemens. The Bus Bar is 200A and has more than 20 breaker slots for breakers. The Main Breaker is a 4-pole 200A.
By 120% rule, if I have an AC feed by a solar system, I can only use a 40A backfeed breaker.
However, I read from somewhere, the author said the total amps of all the breakers can not exceed that 120% rule. I don't think that is correct. The fact is I have 16 branch circuit breakers, a 40A breaker for AC and 70A breaker to a sub panel in my garage that is already over 300A.
What I really think is, if my total usage at any time is more than 200A, the main breaker would simply trip, correct?
In my case, I am not using a lot of power at a time, I believe I can downsize my 200A Main Breaker to 150A, and that will enable me to use a 80A solar backfeed breaker to the Main Service Panel, correct?
Thanks