Nec 1996
bcsmith
I am looking to get information on the code requirerments for installing an 112.5 KVA transformer. The transformer was installed in 1996, thus I need to obtain code info from 1996. I believe the original installation was sized improperly.:mad:
Article 450 has had very few changes to it. I believe table 450.3 is still the same.
What specific questions do you have?
Nec 1996
112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C
If the code hasn't changed much and my math is correct:
Primary OC protection should be 168.75 or 175 breaker size
Wasn't it in the 90's that the NEC let an odd situation out for a cycle.
Wasn't that in respects to 310.16 or another table were wire rating and derating was oddly changed ? I'm sorry again od to the memory!
112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C
Assuming the unit has secondary protection (it should) I come up with an NEC maximum primary overcurrent protection value of 338 amps or a 350 breaker size.
112.5 KVA
4.5 % IZ
HV-480, HA-135
Lv-240, LA-271
Class AA
150 C
Almost, but not quite.
The NEC does not specify a OCPD specific size. Basically for 600V, it says the primary OCPD must not exceed 125% of the primary amps unless you have secondary protection. If you have secondary protection of not more than 125% secondary amps, you are allowed, but not required, to have your primary OCPD larger than 125%.
I have 350 for the secondary OCPD, and I agree with 175 for primary. But is this a 240 delta secondary, or is it one of those wierd high leg thingys that I have never (fortunately) had to deal with? :-? :wink:
Is this the correct math?
PRI
122,500va / (480x1.732)= 135a
135a x 1.25= 169
next higer standard = 175a
SEC
112,500va / (240x1.732) = 270a
270a x 1.25= 337.5A
next standard 350amp
I have to try again. :smile:
PRI
135a x 1.25= 169
next higher standard = 175a
I get this
PRI
135a x 2.5 = 337 amps
next higher standard = 350a
SEC
270a x 1.25= 337.5A
I get the same for the secondary.
I get this
PRI
Bob wheres the 2.5 come from???? Or is it one of those reversed math tricks - like 80% of 125% is the same....
Y*1.25=Z
Z*.8=Y
?..Primary OC protection should be 168.75 or 175 breaker size..?
With Primary and Secondary protection FOR THE Transformer as the Equipment.
Primary protection has no Note 1 for Primary, ie.. ?next higher standard?
Secondary protection does. [240.6 Standard Ampere Ratings.]
Would not Primary OCP be stated at be 150 for the 168.75 or 300 for the 338 calculations.?
(112KVA x 1000)/831,3ph = 135.3 Amp transformer Primary, 169.1 @125% or 338.3 @ 250% if secondary provided.
At this point I Select Wire per 240.4 Protection of Conductors. #1, 75C @ 150A to 300kcmil for the 300A
Is this not correct?
In my opinion there is no correct answer, a lot of it is design decisions.
Your answer will work but it is not the maximum the NEC allows.
In this case the NEC will allow a 350 amp breaker on both the primary and secondary size.