Cavie
Senior Member
- Location
- SW Florida
The subject of FEEDERS came up in a pool bonding thread and got me reading. Art 215.2 (A) (1)
"The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel."
Art 250 deals with Grounding. I spent 1/2 my young adult life understanding the differance between grounded and grounding conductors. Is this a typo? or more of the NEC that I do not understand?
There is more intesting reading in part (A) (1) and (2) if you take the time to read it.
"The size of the feeder circuit grounded conductor shall not be smaller than that required by 250.122, except that 250.122(F) shall not apply where grounded conductors are run in parallel."
Art 250 deals with Grounding. I spent 1/2 my young adult life understanding the differance between grounded and grounding conductors. Is this a typo? or more of the NEC that I do not understand?
There is more intesting reading in part (A) (1) and (2) if you take the time to read it.