2002NEC said:C) In Unfinished Basements.
Where the cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards.
Are the NM's on a beam or joist?2002NECH said:As illustrated in Exhibit 334.1, nonmetallic-sheathed cables installed in an unfinished basement can be run through joists and attached to the side or face of joists or beams and running boards. Section 300.4(D) requires cables that are run parallel to framing members be installed at least 11/4 in. from the nearest edge of studs, joists, or rafters.
lmchenry said:Sorry for the misdirection. My question refers to the cable on the bottom of the joist in the picture you submitted. Section 300.4d requires cables that are run parallel to be 1.25in from nearest edge.
lmchenry said:Sorry for the misdirection. My question refers to the cable on the bottom of the joist in the picture you submitted. Section 300.4d requires cables that are run parallel to be 1.25in from nearest edge.