NEC 2005 - NEC 2011 FIRE PUMP OCPD

Status
Not open for further replies.

AAEB

Member
Location
Southeast Asia
Guys good day!,


Just want to ask the difference between NEC 2011 695.4(b)(2)(a)"the overcurrent protective device(s) shall be RATED to carry indefinitely the sum of the locked-rotor current of the fire pump motor(s)..... against NEC 2005 695.4(b)(1) "the overcurrent protective device(s) shall be selected or set to carry indefinitely the sum of the locked-rotor current of the fire pump motor(s)..... Does this two articles have same meaning?
The way i understand this is "shall be selected or set" is that you can size the OCPB using art. 430.250 (FLA x 1.25%) but setting the long-time delay to withstand the LRC, while " shall be rated" is that you have to size the OCPD based on the LRC plus Jockey pumps and controllers. am i wrong with this?

please enlighten me..:angel:

thanks in advance

AAEB
 