Team-MEI
Inactive, Email Never Verified
- Vancouver, WA
For existing facility feeder(s) or service(s); include the effect of deleted load in total "new load" calculations or not?
Current review process has revealed a rather surprising grey area (it is not a grey area to me) within NEC-2008 220.87.(2) in which an NFPA interpretation needs to occur; this forums' several informed opinions will do nicely though. The reviewer does not allow deleted loads from being included in determining the final or total ?new load? calculations. The current review position seems incorrect to me. The particular code section mentioned does not specify or precisely limit the term ?new load? nor is the term ?load? defined in section 100. However, section 220.60 ?total load? seems to unintentionally but directly apply to this situation. It should be noted in this instance, that not only were certan utilization equipments deleted, but the deleted loads in question also had its entire wiring and associated electrical devices removed per plans.
Do you agree or not? For the purposes of calculating ?new load? according to NEC-2008 220.87.(2); the new load shall be considered to include the combined loads per designated load type being present; consisting of (1) existing peak demand based upon most recent historical meter recordings multiplied by 125% (including those loads which will be deleted) plus any applicable seasonal or periodic adjustment factors if 30-day meter-recording method was used; (2) less any loads being deleted within appropriate demand load type; (3) plus any loads being added within appropriate demand load type.