NEC 2008 701.2 - FPN:
Legally required standby system are typically installed to serve loads, such as heating and refrigeration systems, communication systems, ventilation and smoke removal systems, sewage disposal, lighting systems, and... What space will this lighting serve?

The egress lighting in public corridors that fed out of generator panels, will this lighting belong to emergency system (article 700) or legally required standby system (article 701) above?
 
NEC 2008 701.2 - FPN:
Legally required standby system are typically installed to serve loads, such as heating and refrigeration systems, communication systems, ventilation and smoke removal systems, sewage disposal, lighting systems, and... What space will this lighting serve?

The egress lighting in public corridors that fed out of generator panels, will this lighting belong to emergency system (article 700) or legally required standby system (article 701) above?


Legally required for normal egress, if it where serving sections of a hospital such as an opperating room etc it would need to follow emergency criteria.
 