In the 2011 National Electrical Code is drywall a grounded or non grounded surface for working clearances?
In the 2011 NEC table 110.26(a)(1) condition 2 use to list drywall as a grounded surface, now it seems its silent on the issue.
I guess you can put a voltage tester on the wall and one side in a power source.What is the test of a grounded surface.
I guess you can put a voltage tester on the wall and one side in a power source.
IMHO, it would not be grounded unless it touched something other than just the sheetrock. But verifying that it does not, especially if the tile goes all the way down to a concrete floor, for example, or if wire lath in the tile bed touches a screw penetrating the sheetrock, or if the grout or mastic is conductive. (I would not necessarily expect the drywall guys to mud over screws that will be covered by tile anyway, for example.)It not in the MV table back to 2005. Anyway I wonder if you have tile on a sheetrock wall would that be considered grounded. It seems to say that since it is not specific.
Has anyone yet noted that Section 110.26 (A)(1) and its Table don?t apply to Medium Voltage switchgear; nor likely to the back of it?Working clearances behind a MV 13.8 gear. I might have seen it in a hand book that the Inspector had.
Has anyone yet noted that Section 110.26 (A)(1) and its Table don?t apply to Medium Voltage switchgear; nor likely to the back of it?
Here's how to tell:
Stand on an insulating mat. Grab a hot wire. Touch the drywall. If you survive, it's not grounded.
I will say that many things that are non conductive below 600 volts are not necessarily considered non conductive above 600 volts.
Here's how to tell:
Stand on an insulating mat. Grab a hot wire. Touch the drywall. If you survive, it's not grounded.