jasonziegler
Member
- Location
- Council Grove, KS
Hello
This is my first post. I am a newly licenced electrician. I have been doing Plumbing and HVAC for around 10 years and recently got my electrical license. I recently did a job on a new atm had some problems with the city code officials on interpretation of code. I send a question to the NFPA and never got the response from them so I thought I would try here. I have copied what I sent them
Hello
I am trying to find some codeinterpretation and I am having some disagreement with my local city officialsabout this.
Our city code has the 2011 InternationalElectric Code adopted.
I recently did a job and had undergroundservice feed from the alley to a meter can that was set on a H frame outside anatm. I attached a 200 amp service disconnect panel directly to the meter via a2” zinc offset nipple. I had 2 ground rods that was installed before theconcrete was poured and encased in the concrete. I ran the ground wire from theground rods to the meter because that is were our local power company (formerlywestar energy now evergy) requires it. I ran my 2 hot wires and my neutralwires to the service disconnect panel and bonded the service disconnect withthe bonding screw provided. This is were the issue came up. I was told by mycity officials that I have to ground the service disconnect panel to the groundwire to the meter or a separate ground rod to the service disconnect. My understanding of the code thatthis would be classified as Paralleling the neutral. They required me to run aground wire from the service disconnect panel to and attached it to the groundwire below the meter can.
Here are the reason is believe this iswrong:
Reference 250.142 Use of Grounded CircuitConductor for Grounding Equipment
230.66 Marking
States that an individual meter socketenclosure shall not be considered service equipment
I have attached a rough drawing of what Idid before they required me to run the separate ground wire from the ground barthat they still wanted bonded and attached below the meter to the ground wirewith a split bolt connector.
I found this video from Mike Holt aboutit as well
https://youtu.be/wyPTtN6QjzQ
If I am wrong I can accept that and moveon, but I have talk to several electrical friends from other city’s that say Iam right about this. But if I am right I want to get them corrected so theyquit telling everyone else how to do it. I am the only one that has argued withit.
Thank you.
Jason Ziegler
This is my first post. I am a newly licenced electrician. I have been doing Plumbing and HVAC for around 10 years and recently got my electrical license. I recently did a job on a new atm had some problems with the city code officials on interpretation of code. I send a question to the NFPA and never got the response from them so I thought I would try here. I have copied what I sent them
Hello
I am trying to find some codeinterpretation and I am having some disagreement with my local city officialsabout this.
Our city code has the 2011 InternationalElectric Code adopted.
I recently did a job and had undergroundservice feed from the alley to a meter can that was set on a H frame outside anatm. I attached a 200 amp service disconnect panel directly to the meter via a2” zinc offset nipple. I had 2 ground rods that was installed before theconcrete was poured and encased in the concrete. I ran the ground wire from theground rods to the meter because that is were our local power company (formerlywestar energy now evergy) requires it. I ran my 2 hot wires and my neutralwires to the service disconnect panel and bonded the service disconnect withthe bonding screw provided. This is were the issue came up. I was told by mycity officials that I have to ground the service disconnect panel to the groundwire to the meter or a separate ground rod to the service disconnect. My understanding of the code thatthis would be classified as Paralleling the neutral. They required me to run aground wire from the service disconnect panel to and attached it to the groundwire below the meter can.
Here are the reason is believe this iswrong:
Reference 250.142 Use of Grounded CircuitConductor for Grounding Equipment
230.66 Marking
States that an individual meter socketenclosure shall not be considered service equipment
I have attached a rough drawing of what Idid before they required me to run the separate ground wire from the ground barthat they still wanted bonded and attached below the meter to the ground wirewith a split bolt connector.
I found this video from Mike Holt aboutit as well
https://youtu.be/wyPTtN6QjzQ
If I am wrong I can accept that and moveon, but I have talk to several electrical friends from other city’s that say Iam right about this. But if I am right I want to get them corrected so theyquit telling everyone else how to do it. I am the only one that has argued withit.
Thank you.
Jason Ziegler