hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows building layout bottom left corner, electrical room detail bottom right corner and Riser at top.

Building layout shows Vacant space which has not been filled and Tenant A space occupancy type B. In the top middle of layout is electrical room.

Electrical room detail shows main service SWGR as soon as one enters from outside door up top and main service MDP behind middle wall.

Riser shows two main service gears: MDP and SWGR fed from one utility transformer.

Riser shows MDP has 800A main service disco and feeds thru feeder breakers tenant A loads as well as Vacant Space load. MDP has one POCO meter and rest are customer owned sub meter.

Riser shows SWGR has one POCO meter, 600A main service fused disco and feeds thru feeder breakers three house panels loads and all building RTUs including RTUs for Tenant A and vacant space.

Please note that main service disconnects of MDP and SWGR are not grouped. Set of service entrance conductor run to MDP electrical room and separate set of service entrance conductor run to SWGR electrical room all from one utility transformer.

Question is does NEC 2014 section 230.40 exception number 1 apply set of service entrance conductors running to group of occupancies so that both gears can be Not grouped or 230.40 exception no. 1 does not apply and both gears need to be grouped?

4c858e96e9b31623dee08f0284a56019.jpg



Sent from my iPhone using Tapatalk
 
Attached sketch shows building layout bottom left corner, electrical room detail bottom right corner and Riser at top.

Building layout shows Vacant space which has not been filled and Tenant A space occupancy type B. In the top middle of layout is electrical room.

Electrical room detail shows main service SWGR as soon as one enters from outside door up top and main service MDP behind middle wall.

Riser shows two main service gears: MDP and SWGR fed from one utility transformer.

Riser shows MDP has 800A main service disco and feeds thru feeder breakers tenant A loads as well as Vacant Space load. MDP has one POCO meter and rest are customer owned sub meter.

Riser shows SWGR has one POCO meter, 600A main service fused disco and feeds thru feeder breakers three house panels loads and all building RTUs.

Please note that main service disconnects of MDP and SWGR are not grouped. Set of service entrance conductor run to MDP electrical room and separate set of service entrance conductor run to SWGR electrical room all from one utility transformer.

Question is does NEC 2014 section 230.40 exception number 1 apply set of service entrance conductors running to group of occupancies so that both gears can be Not grouped or 230.40 exception no. 1 does not apply and both gears need to be grouped?

4c858e96e9b31623dee08f0284a56019.jpg



Sent from my iPhone using Tapatalk

Edited post#1 following part: SWGR feeds building RTUs not sure if they are vacant or Tenant A but building has Tenant A and Vacant space single floor.
 