2-180 Log #3263 NEC-P02 Final Action: Accept in Principle
(210.52(G))
________________________________________________________________
TCC Action: The Correlating Committee understands that the panel
action on this proposal modifies the panel action on Proposal 2-178a.
Submitter: Brian E. Rock, Hubbell Incorporated
Recommendation: Add new text to 210.52(E)(1) to read as follows:
210.52 Dwelling Unit Receptacle Outlets.
[main requirement of 210.52 and 210.52(A) through 210.52(F) unchanged by
this Proposal]
(G) Outlets in Basements, Garages, and Accessory Buildings. For a one-
family dwelling, the following provisions shall apply:
(1) At least one receptacle outlet, in addition to those for specific equipment,
shall be installed in each basement, in each attached garage, and in each
detached garage or accessory building with electric power. For receptacle
outlets inside of attached and detached garages, branch circuit(s) supplying
garage receptacle outlets not installed for specific equipment shall have no
other outlets.
(2) Where a portion of the basement is finished into one or more habitable
rooms, each separate unfinished portion shall have a receptacle outlet installed
in accordance with this section.
[remainder of 210.52 unchanged by this Proposal]
Substantiation: Electric vehicles (EVs) and plug-in hybrid electric vehicles
(PHEVs) however are becoming far more prevalent; government goals and
incentives, coupled with petroleum pricing and global warming consequences,
in coming years will augment this trend amongst dwelling occupants. 15- and
20-ampere garage receptacles are commonly on branch circuits shared by other
outlets in the dwelling unit. NEC? 625.14 however correctly recognizes at 15
and 20 amperes that an electric vehicle charging load is a continuous load
(persists longer than 3 hours to full recharge). Since even so-called Level 1
electric vehicle supply equipment (EVSE), cord-and-plug-connected, is rated
typically at the maximum allowable under Table 210.21(B)(2), 12 amperes, the
garage receptacles required by 210.52(G)(1) that can be connected to the EVSE
should be on branch circuits with no capacity exceeding the Table 210.21(B)(2)
maximum diverted to other outlets on the same branch circuit.
Panel Meeting Action: Accept in Principle
Add the following sentence to (1) of 210.52(G):
?The branch circuit supplying this receptacle(s) shall not supply outlets
outside of the garage.?
The panel recognizes that this revision is in addition to the changes made by
2-178a.
Panel Statement: See the action taken on 2-178a.
The panel has added a provision to limit the circuit supplying the garage
outlets to supply only those outlets in the garage.
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
Comment on Affirmative:
HILBERT, M.: Continue to accept in principle but consider revising the
panel?s meeting action as follows:
The branch circuit supplying this receptacle(s) shall not supply other outlets.
As revised by the ROP meeting action, lighting and other outlets could be
supplied from the receptacle circuit if they were in the garage which is beyond
the recommendation. The submitter?s proposed text limited this branch circuit
to just the 210.52(G) receptacle outlet(s.) This would make sense if this change
is to provide a means for EV charging.
ORLOWSKI, S.: NAHB urges the panel to reject this proposed change. The
concern for providing a dedicated branch circuit for electric vehicle charging
and not allowing any other outlets on this dedicated branch circuit was
addressed in CP212. If this proposal should be approved, it would now require
an additional branch circuit to feed the receptacle(s) in the garage and no other
receptacles. There has been a long standing practice in the code to allow a
single branch circuit to supply the required receptacles in the garage, the
unfinished basement and the
exterior receptacles. Why are we now going to require the garage receptacle(s)
to be on a dedicated branch circuit serving no other outlets and not permit them
to feed a exterior receptacle or a security light. No information was provided to
justify this change nor was any data provided to show that the current
allowance by the NEC was a hazard.