I'm unaware of a fire alarm system that uses line voltage on the detection devices. Or a line voltage smoke detector that ties to a interconnected alarm panel. Perhaps you can provide make/model of proposed device/panel you propose using. My connection to an alarm system provider indicated no such animal.
Your other thread you suggest the intended application is in a multiple unit assisted living facility, that requires, at least here, a tie into local emergency response not just local alarm. Assuming that is your reason to use a FACP, and also your seaming intent to use the "cheaper" smoke alarms and hoping to tie them to the panel.
The exception you quote to use is strictly for a FACP and the LV devices associated with an alarm system. They exempt the alarm system because they want no "neusiance" trip to disable an alarm system. That too is why we install such systems on a dedicated circuit not to be used by any unrelated devices. The exception quoted, as of the 2017 code (the last codes training I was part of) specifies a standard smoke/CO detector or series of same does not make a fire alarm system for exemption purposes.
Agreed