Please see attached sketch. I have enclosed circuit breaker 0 which feed meter stack. The meter stack has feeder breakers 18 of them AIC rating of 10kA which feed MLO panelboards 18 of them in apartment each dwelling unit. The MLO panelboard feed feeder breaker 10ka hvac load MCA of 20A.
Meter stack feeder breaker is suppose to be series rated with MLO panelboard feeder breaker. Also the meter stack feeder breaker is series rated with ECB Bkr 0.
However the way I see it is series rating would Not be allowed between meter stack feeder breaker and panelboard feeder breaker due to NEC 2014 section 240.86(C). HVAC MCA is 20A. 20Ax17=340A which is greater than 1% of 10kA.
Following questions:
1. Am I correct or incorrect that NEC 2014 section 240.86( C) would not allow series rating between feeder breaker and MLO panelboard feeder breaker?
2. Would series rating apply to ECB breaker 0 and meter stack feeder breaker or not NEC 2014 section 240.86(C)?
Meter stack feeder breaker is suppose to be series rated with MLO panelboard feeder breaker. Also the meter stack feeder breaker is series rated with ECB Bkr 0.
However the way I see it is series rating would Not be allowed between meter stack feeder breaker and panelboard feeder breaker due to NEC 2014 section 240.86(C). HVAC MCA is 20A. 20Ax17=340A which is greater than 1% of 10kA.
Following questions:
1. Am I correct or incorrect that NEC 2014 section 240.86( C) would not allow series rating between feeder breaker and MLO panelboard feeder breaker?
2. Would series rating apply to ECB breaker 0 and meter stack feeder breaker or not NEC 2014 section 240.86(C)?